100201-1026 EST
Some additional points on neutral problems.
For the first part of this discussion assume a 120 V branch circuit originates at a breaker panel. There are two wires, a neutral and a hot, from this panel for the branch circuit. There are no incorrect connections from this circuit to another circuit.
If the voltage at the breaker panel is invariant, is always 120, then no poor connections in either the hot or neutral parts of the branch circuit can cause an increase in the voltage at the load. From a transient point of view, fractional part of a cycle, if there was substantial inductance in the circuit, then on turn off of current in the circuit there could be a momentary increase in voltage. Sufficient energy from this in a residential application is essentially zero relative to an incandescent lamp.
Where neutral problems exist they result from a 240 V center tapped transformer supplying a pair of opposite phases for 120 V circuits. In this case a common neutral part of the system, most likely between the neutral buss bar and the transformer center tap, with high resistance in the common neutral can cause unbalanced supply voltages to branch circuits.
If on the load side of the panel neutral buss bar you share a neutral with two or more branch circuits and at least one of the circuits uses an opposite phase, then a high resistance in the load side common neutral can be a source of problems.
Otherwise a high resistance neutral does not cause high voltage problems.
To visualize this draw a center tapped transformer, a small resistance in the neutral wire, and two load resistances connected to the opposite phases. Now do circuit analysis.
.