Light Pole at Doctor's Office

Status
Not open for further replies.

xguard

Senior Member
Location
Baton Rouge, LA
My kids and I were walking around at an after hours care clinic while my wife was inside being seen. It was impossible for me not to see this right next to the parking spots. All the poles were basically like this. I got an email for the manager (politely I may add). I just wanted to drop them a friendly line warning them about this. The biggest issue to me is the missing cover. I see covers missing all over the place but this one being a couple feet from a parking space bothered me more than most. Also, there's NM-B cable inside the light pole. You probably can't tell from the photo but it had just rained and all the wiring was wet. I don't deal with NM cable in commercial but from the looks of it, it can only be used in dry locations. Is this right? Also, assuming the light pole actually had the hand-hole cover installed (like they rarely are), and the wires weren't wet (like they were), could the inside of a light pole be considered a dry or damp location? I realize the inside of a raceway in a wet location must be considered a wet location. I would assume the same is true of a pole.
 

Attachments

  • 20190504_124136 - Copy.jpg
    20190504_124136 - Copy.jpg
    118.7 KB · Views: 2
  • 20190504_124342 - Copy.jpg
    20190504_124342 - Copy.jpg
    62.5 KB · Views: 2
NM in the last 30 years has been THHN/THWN, but just not labelled as such.


If it makes you feel better I've seen tons of NM in conduit underground to detached garages from the 70s without issue on the insulation. At least on the exposed portions I had access to.
 
Inside is wet location because condensation is likely to form in there.

Bonding the pole and having a cover are bigger concerns to me than the NM cable - though it is not a wet location cable.
 