Light pole base, wet or damp location?

Status
Not open for further replies.

nietzj

Senior Member
Location
St. Paul, Minnesota
Occupation
Electrician
Would you consider a standard light pole base with a cover for access a wet or damp location? The AHJ is questioning if my splices should be treated as wet locations terminations. I have always considered a light base as a damp location. I guess there could be a flood someday but that seems ridiculous to wire for that scenario. Help!
 

nietzj

Senior Member
Location
St. Paul, Minnesota
Occupation
Electrician
So for all practical purposes the AHJ can call this a wet or damp location. As long as I use dual rated conductors THHN / THWN (or any other approved conductor) and splice with gel filled wire nuts listed for wet locations I should be fine.
 

Cow

Senior Member
Location
Eastern Oregon
Occupation
Electrician
I've only ever seen regular wire nuts in light poles, it's also what we use.

I point them up though, like an umbrella, just in case though....
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Would the splice compartment in a light pole be the same as the inside of a junction box in a wet location?
 

jap

Senior Member
Occupation
Electrician
I've only ever seen regular wire nuts in light poles, it's also what we use.

I point them up though, like an umbrella, just in case though....



Just like most all normal electricians do.


JAP>
 

jap

Senior Member
Occupation
Electrician
Would the splice compartment in a light pole be the same as the inside of a junction box in a wet location?


I would say no. A junction box in a wet location is much more prone to retaining water whether it be by drivin rain or simple condensation if weep holes are not drilled into it.

A splice made inside the compartment of a light pole is much better since the splice is most always 6 or 8 inches above the pole base, and, any moisture that may accumulate inside the pole ends up draining out the bottom on it's own. :)

JAP>
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I would say no. A junction box in a wet location is much more prone to retaining water whether it be by drivin rain or simple condensation if weep holes are not drilled into it.


JAP>

Does the NEC consider the inside of the box a wet or damp Iocation?
 

rcarroll

Senior Member
Does the NEC consider the inside of the box a wet or damp Iocation?
IMO, If it did, we'd have to use all wiring suitable for wet locations, Weather Resistant breakers & fuses for all panel installed outdoors. :D
All the light poles I've wired, all the covers had gaskets. I was never required to have water proof splices, nor do I require them on inspections.
 

jap

Senior Member
Occupation
Electrician
Does the NEC consider the inside of the box a wet or damp Iocation?

I guess that would all depend on the type of box being installed , but, if a box was installed that was rated for a wet or damp location, I would hope not.


JAP>
 

jap

Senior Member
Occupation
Electrician
IMO, If it did, we'd have to use all wiring suitable for wet locations, Weather Resistant breakers & fuses for all panel installed outdoors. :D
All the light poles I've wired, all the covers had gaskets. I was never required to have water proof splices, nor do I require them on inspections.

Your going to have to use wiring suitable for a wet location anyway, because the raceway leading to the box or pole light is considered a wet location.

The OP's talking about the termination method being used, not the conductors.

JAP>
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I agree, wet location conductors but the splice point in the interior of the pole base should be a dry location just like the inside of a junction box.
 

jap

Senior Member
Occupation
Electrician
I guess one could argue that the pole itself was an outdoor raceway, which just as the inside of an outdoor conduit, was considered a wet location before they cut the hand hole and cover into it making it into nothing more than a long cylindrical shaped wet location rated junction box so that normal wire nuts could be used. :)


JAP>
 