OK it often comes up that engineers have specified ground rods at light poles.
The standard answer is that they are not required by the NEC.
What happens when there is more than one circuit at the pole, wouldn't 250.32(A) require a grounding electrode?
One could be for a receptacle outlet and the other for the lights. Or there could be two circuits on one pole.
The standard answer is that they are not required by the NEC.
What happens when there is more than one circuit at the pole, wouldn't 250.32(A) require a grounding electrode?
One could be for a receptacle outlet and the other for the lights. Or there could be two circuits on one pole.
250.32 Two or More Buildings or Structures Supplied from a Common Service.
(A) Grounding Electrode. Where two or more buildings or structures are supplied from a common ac service by a feeder(s) or branch circuit(s), the grounding electrode(s) required in Part III of this article at each building or structure shall be connected in the manner specified in 250.32(B) or (C). Where there are no existing grounding electrodes, the grounding electrode(s) required in Part III of this article shall be installed.
Exception: A grounding electrode at separate buildings or structures shall not be required where only one branch circuit supplies the building or structure and the branch circuit includes an equipment grounding conductor for grounding the conductive non?current-carrying parts of all equipment.