Re: Light Poles and Grounding Electrodes
I know this subject has been beat to death, and at my former employer I was forced to integrate the light poles in the parking lots into the building GES system. The main reason for doing this was to add protection to the security equipment mounted a top of the poles.
As I asked before what is the difference between a light pole and a communication tower. Ron and John hit on some of the differences. Ron pointed out shouldn?t the ground rod be integrated into the building GES if used, and John pointed out the pad provides a sufficient Ufer ground and a rod would be in the sphere of influence. To John I would agree and disagree. If the rod were set beside the pole I would agree. If the rod were set below the pad, I disagree, but it is a mute point.
So the main differences between a light pole and tower is 1. Tower GES system is integrated into building and property GES system. 2. All signal cable shields and power are multi-bonded to the tower especially where they leave the tower. 3. Most importantly all cables entering the building enter at approximately the same point the AC service and all outside plant cables employing SPG and using a surge protection devices bonded to the GES to discharge the ungrounded conductors.
So what techniques can be economically employed and what is not necessary:
1. IMHO an additional rod is not necessary, as I do not believe it adds any value unless it can be integrated into the building GES via radial, it?s just a light. However there is no real harm done by adding one other than expense, and if used set it below the pad as not to be in the sphere of influence.
2. Most importantly, if lightning is a concern, simply add a TVSS or surge device where the circuit enters the building and referenced to the GES, and another one in the panel serving the branch circuit. It is preferable the circuit enter near where the AC service enters to aid GES access. As Charlie Tuna pointed out even if the pole does have a rod, if the pole is struck, a charge will be induced onto the ungrounded and grounded circuit conductors, and will appear inside the building looking for a place to equalize/discharge. Give it a place or two to discharge rather than letting it find it?s own path through the distribution system and/or equipment.
OK, I will shut up now