New User
- Location
- Denver, CO
- Occupation
- Contractor
Does the NEC require new light poles on existing older caissons to be connected to a ground rod? They are bonded to the equipment grounding conductor.
Not required. But, if the rod is already there why fight over it.Does the NEC require new light poles on existing older caissons to be connected to a ground rod? They are bonded to the equipment grounding conductor.
It’s often done but serves no purpose, and the subject creates substantial discussion.
What purpose do you think it might serve?What is reasoning of it not serving any purpose?
JAP>
Maybe it'll get a lightning strike in the dirt a little sooner.What purpose do you think it might serve?
What makes you think ground rods have anything to do with lightning?Maybe it'll get a lightning strike in the dirt a little sooner.
JAP>
What makes you think they don't?What makes you think ground rods have anything to do with lightning?
They do not serve any purpose with respect to lightning at all.What makes you think they don't?
JAP>
I guess if you didn't connect the end of a grounding electrode conductor to an actual grounding electrode in the earth such as a ground rod or the like, no it wouldn't.They do not serve any purpose with respect to lightning at all.
It seems highly unlikely that the electrical system would be grounded at each pole. That would be a code violation.240.4(A)(1) Electrical System Grounding.
Electrical systems that are grounded shall be connected to earth in a manner that will limit the voltage imposed by lightning, line surges, or unintentional contact with higher-voltage lines and that will stabilize the voltage to earth during normal operation.
It seems highly unlikely that the electrical system would be grounded at each pole. That would be a code violation.
.
No, it is not. The provision that was quoted in a previous post though does refer to connecting the electrical system to ground 250.4(A)(1), and nothing directly to do with the EGC.A ground rod driven at a pole light and connected to the equipment grounding conductor pulled to and connected to that pole is not re-grounding the system.
JAP>