I had an "engineer" call me today asking about the 25-ohm resistance for 2 rods installed at a lighting pole. His question was what they should do if two rods did not provide the "required" 25-ohms resistance? I told him to do nothing, once you drove 2 rods you were done, in fact you did not need to drive any rods at a pole. He told me I was wrong, that they were required by the NEC. That without a low resistance path to the earth a circuit breaker would never trip. I referred him to 250.32(A) Exception. He started stammering and said that he was going by "another NFPA document that requires lightning protection at each pole". He was very disappointed that I would not support his completely erroneous conclusions. It is a shame that the term "engineer" can mean anything from a clueless flunky to some of the most brilliant minds in the world...