Although the armored portion may be FMC this is not being used as a raceway it's a factory wiring assembly so no 360° limit. Why would someone call this out for a whip in the first place? :slaphead:
I agree, I was very skeptical when the inspector said that, hence this discussion. Problem is though is that we'll just do what he wants, take the loop out and then it will look terrible with the whip just hanging up there. My boss didn't want to argue it with him. Oh well...

Sent from my SCH-I435 using Tapatalk
 
I agree, I was very skeptical when the inspector said that, hence this discussion. Problem is though is that we'll just do what he wants, take the loop out and then it will look terrible with the whip just hanging up there. My boss didn't want to argue it with him. Oh well...

Sent from my SCH-I435 using Tapatalk

That is the dilemma we all deal with every day. At a minimum, your boss could send an email asking for a code section that requires a UL listed wiring assembly to comply with whatever NEC rules he is saying requires you to install it differently. Then if he comes back with a bogus FMC rule, let it drop.
 
I said I'd post a pic of the whip. Fairly basic install.
a0e021f7fe206b63932668ba7cd84d26.jpg


Sent from my SCH-I435 using Tapatalk
 
Be happy it’s the whips, I think he could have asked for the conduit to be spaced further from the deck. Those roofing screws would fall under 358.12(1)

Dang pictures...

Good catch, isn't it odd that the inspector dwells on something inane, while an actual important code violation hits him in the face.
 
Be happy it’s the whips, I think he could have asked for the conduit to be spaced further from the deck. Those roofing screws would fall under 358.12(1)

Dang pictures...
Never thought of that. Would that still be considered a potential for physical damage since the pipe was run after the roof was finished?

Sent from my SCH-I435 using Tapatalk
 
Never thought of that. Would that still be considered a potential for physical damage since the pipe was run after the roof was finished?

Sent from my SCH-I435 using Tapatalk

The roof will probably be replaced at some point.
Code says "Where, during installation or afterward, it will be subject
to severe physical damage."
 
Be happy it’s the whips, I think he could have asked for the conduit to be spaced further from the deck. Those roofing screws would fall under 358.12(1)

Dang pictures...

Never thought of that. Would that still be considered a potential for physical damage since the pipe was run after the roof was finished?

Sent from my SCH-I435 using Tapatalk

Look at 300.4(E). It is a bit more specific.
 