My clarification issues weren't really clarification issues after all. I do understand thw whol calculating the amps deal, and I know that is what you base you whole circuit off of, is the number of amps to that circuit.
The whole reason this question of mind started is that I couldn't figure out what the engineer was doing and how he figured out how many fluroscent lights he could put on a circuit. Now that I have been told time and time again, this many with room to spare I understand.
But the I continued to question this further with the deal on the Continuous load and that they need to times everything that is like this situation by 125%. That's where I got resistance. 2 people in that meeting that I wrote about a while back never heard of doing it. I told both of them, it's in the CODE! Don't you follow the CODE????
And since that meeting, nothing else has been said about calculations, etc. for projects, and I'm not going to bring anything up becuase A) I think he doesn't want to be proved wrong B) I think he can't handle being outsmarted by a women C) stuck in the ways and won't change.
So I decided to continue this quest by myself and keep stuff to myself. I just recently talked to someone that is a rep of some kind for Advance Ballasts. I told him about the 125% factor that you use on the amps from the ballast information. He also hasn't heard of this. He was going to do some digging, and get in contact with a "old jigger" that's been with Advance Ballasts many years. Since he called yesterday, I have not had a call back. So it will be interesting to see what they come up with.
Now, you take that input watts of the ballast (which has the PF factored in) and divide it by your source voltage to get your amps for that light fixture. From those amps you take 125% to get your final amount of amps, and then start adding them up to do your circuits.
That's it, correct? Nothing more, nothing less. and seems so easy too!
As far as the panelboards currently being shown for the drawings I put together and go out the door, I have no control over. If that engineer no longer works there, then I will suggest and/or implement a better panelboard schedule that shows information an electrician would really think is necessary. Until that point however, I put up with what I see.
Thanks again, for everyone's help. I guess I didn't realise this was out there, and will "ponder" with the inspector I know in 2 months about this formula. I'm just so curious to hear his opinoin.