We are bidding a fuel distribtion system. The pump room will have light fixtures that are suitable for the atmosphere. These fixtures will be piped together with galv. rigid conduit. My question is, are sealoffs required between each fixture? I read that the fixture wiring enclosure will be enclosed and separate from the lamp compartment. Please let me know your thoughts.
jackman
I am assuming you mean that that the luminaire has an integral "factory sealed" terminal box. If that is correct, see Section 501.15 (A)(1)
Exception part (3). Note the
Exception has its own 2" entry disqualifier. Also read the text immediately following the
Exception.
Basically, the question is whether each luminaire needs to be sealed individually. If they meet 501.15 (A)(1)
Ex part (3), they aren't required to be sealed individually and nothing is required between them either. If they don't meet the
Exception, their individual seals are all that is required. It is possible that one intermediate seal could be omitted under Section 501.15(A)(3)/