If a lighting contactor was designed as Nema 3, with a 60A resistive heating load the 250% max rating is 150A.  The Nema 3 spec provided 100A service which would suffice for 125%, but not the 250%.  The manufacturer supplied a Nema 4, 200 A contactor with a 200A CB instead of the 90 A CB spec'd.  Is this ok, it doesn't seem to meet code, but I am in the field and do not have the proper tools.