Re: Lighting Contactors
For connection you do get a common, open and close terminal. Internal switching makes it work with one coil.
Article 100
[ November 13, 2005, 07:56 AM: Message edited by: iwire ]
Ascos have only one coil, it is used for both opening and closing.Originally posted by augie47:
then there is also the "unlatch" coil which you momnentarily energize to cause the contacts to change.
For connection you do get a common, open and close terminal. Internal switching makes it work with one coil.
Approved is not the same as listed.Originally posted by infinity:
I have heard of installations such as this. However I would think that this would violate 700.3 unless that relays were approved for use on emergency systems.
700.3 Equipment Approval.
All equipment shall be approved for use on emergency systems.
Article 100
I am sure the RIBs would be approved if the lights they control come on when the RIB fails. In other words wired normally closed.Approved. Acceptable to the authority having jurisdiction.
[ November 13, 2005, 07:56 AM: Message edited by: iwire ]