Lighting: Control Outdoor w/ Dusk and Time
Hey guys, Thank You for all the input - - SOLVED - -
Its been a bit, didn't want to reply until I was complete & tested over time
Solved this one, been running for over 3 months, Works Great
Thought I'd post Project Details for others, hope this helps the community.
Also I created a Spreadsheet to record setup and programming data if anybody wants it for there use. LMK
Wasn't sure how to upload the file because upload file type rules, but text/table below contains the format/info.
1.) Application/ Project: Light Timing, Morning & Night periods, No Photo-eye, with offsets for early/late Dusk/Dawn Functionality
Shore Lights, Globe Lighting on poles already , 120VAC/20A single circuit, ~10-12 Poles, A19 lamps - 2700K - 1500l (~230mA/per)
Complete circuit currently on Photo Eye/SW (Dusk to Dawn) [Removed]
Requirements:
1.) Turn ON15-30 minutes before Dusk everyday.
2.) Turn OFF at approx. 1:00AM
3.) Turn ON ~1 hour before Dawn
4.) Turn OFF at Dawn
5.) Set it and forget it system : - )
2.) Product Choice, Intermatic ST01, 7-day Programable In-Wall Timer
3.) Removed Existing PE and installed ST01
4.) Unit included 'Manual Override SW input, Installed Conduit SG Box, SPST Sw., Wired into ST01 input
5.) ST01 Setup (Menu)
SETUP
HourCurrent/Actual
MinuteCurrent/Actual
YearCurrent/Actual
MonthCurrent/Actual
DateCurrent/Actual
DayCurrent/Actual
DSTAuto
ZoneCT
CountryUSAActual Long/Lat, 45.0464° N, 87.2971° W
Latitude450Note: No Decimal point
Longitude873Note: No Decimal Point, rounded up
Dawn Offset05:28:36 AM06:00:00 AM
Dusk Offset08:22:52 PM07:45:00 PM
6.) Program ST01 (Menu Steps)
For Clarity, Items in BOLD indicate
Entry/Display is Flashing
BOLD = FLASHING
Edit
Display shows the followingButton 2 Press
04:00:00 AMAll01ON/OFF
ONAll01ON/OFF
04:00:00 AMAll01ON/OFFSet Time
04:00:00 AMAll01ON/OFFOffset adjusts
Auto… SAVE … (Briefly Displayed)
04:00:00 AMAll01'+
04:00:00 AMAll02ON/OFF
DAWNAll02ON/OFF
OFFAll02ON/OFF
DAWNAll02ON/OFF
DAWNAll02ON/OFF
DAWNAll02'+
DUSKAll03ON/OFF
ONAll03ON/OFF
DUSKAll03ON/OFF
DUSKAll03ON/OFF
DUSKAll03'+
DUSKAll04ON/OFF
12:00:00 PMAll04ON/OFF
OFFAll04ON/OFF
12:00:00 AMAll04ON/OFFSet Time
12:00:00 AMAll04ON/OFFOffset adjusts
12:00:00 AMAll04MODE
Current TimeAuto
Current TimeAuto
unit