What Dick is stating is somewhat true. Per NEC 501.130(B):
(1) Luminaires. Where lamps are of a size or type that
may, under normal operating conditions, reach surface temperatures
exceeding 80 percent of the ignition temperature
in degrees Celsius of the gas or vapor involved, luminaires
shall comply with 501.130(A)(1) or shall be of a type that
has been tested in order to determine the marked operating
temperature or temperature class (T Code).
The NEC Handbook and the NFPA's book "Electrical Installations in Hazardous Locations" both explain that "previously called Vaportight" fixtures are acceptable for C1D2 use. So if the fixture surface temp exceeds 80 of the ignition temp of whatever the hazard is then it has to be explosionproof or marked with a T Code. I am not sure how you would get a T Code unless it was listed for C1D2 but still Dick is techinically correct. The NEC does not necessarily REQUIRE that a luminaire be listed as C1D2.
Gadfly:
Division 1: always present (not techincally correct- "can exist normal operating conditions" is the correct phrase and no they are not quite the same thing)
Division 2: present on occasion or if equipment fails or something breaks (good explanation- "in case of accidental rupture or breakdown of such containers or systems or in case of abnormal operation of equipment")
So a gas/vapor may still be "present on occasion" but if it is so due to normal conditions then it would be a C1D1. It does not have to be "always present" to qualify a C1D1.
Thanks, HEY!!!! I got an ally, the sky is going to fall for sure,,,,,,,its all for a good cause and learning curve.