ok so bear with me...What I have is a new detached residential pool house we are wiring...the owner is worried about the attic above molding from all the moisture sooo the heating company is making the attic a wild return to keep air flow rolling through up there...I see per 300.22 that I now have to run MC cable up there now but can't seem to figure from the wording about lighting....
The pool house will have a 10' flat sheetrocked ceiling throughout and I want to install recessed cans all over. Now knowing the whole attic is a plenum area can I put the cans in??? or do I have to frame sealed boxes around all of them or ????? I guess I've never had the attic of a residential job a plenum and am confused on what I have to do....like I said I know I have to use MC for wire but what about lighing boxes and cans?? anything I have to know???? thanks guys (ohh and gals)
The pool house will have a 10' flat sheetrocked ceiling throughout and I want to install recessed cans all over. Now knowing the whole attic is a plenum area can I put the cans in??? or do I have to frame sealed boxes around all of them or ????? I guess I've never had the attic of a residential job a plenum and am confused on what I have to do....like I said I know I have to use MC for wire but what about lighing boxes and cans?? anything I have to know???? thanks guys (ohh and gals)