lighting load on a 20 amp branch circuit

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
If the load truly fits the definition of continuous found in Article 100 you will be required to figure it at 125% / 80% whichever way you want to look at it.

That being said, those are code minimums not always the same as good design.
 