How much lighting load can I put on a 20 amp circuit at 277 volt?
roger Moderator Staff member Location Fl Occupation Retired Electrician Apr 29, 2008 #2 5,540 watts. Roger
iwire Moderator Staff member Location Massachusetts Apr 29, 2008 #3 roger said: 5,540 watts. Click to expand... I agree. :smile:
K KAEnoch Member Apr 29, 2008 #4 Thanks Roger. For continuous load I should multiply 5,540 by 80% which is equal to 4,432 watts, correct?
iwire Moderator Staff member Location Massachusetts Apr 29, 2008 #5 If the load truly fits the definition of continuous found in Article 100 you will be required to figure it at 125% / 80% whichever way you want to look at it. That being said, those are code minimums not always the same as good design.