Section 680.22(B)(4)
(4) GFCI Protection in Adjacent Areas. Luminaires,
lighting outlets, and ceiling-suspended (paddle) fans installed
in the area extending between 1.5 m (5 ft) and 3.0 m
(10 ft) horizontally from the inside walls of a pool shall be
protected by a ground-fault circuit interrupter unless installed
not less than 1.5 m (5 ft) above the maximum water
level and rigidly attached to the structure adjacent to or
enclosing the pool.
 