lighting on gfci breaker issues

Status
Not open for further replies.

mooreaaryan

Member
Location
Bakersfield CA
Occupation
Electrician
we are doing a control tower for branch of the military. they have asked us to put the lighting circuit on a gfci breaker. we complied and now the lights trip. the lights are led the load is a total of 11amp the gfci breaker is a 2oamp has anyone had problems putting lights on gfci breakers
 
I don't see why the load being lighting would have anything to do with it. If the breaker trips immediately check for a fault from neutral to ground. Beyond that, it may be possible that one or more drivers has some leakage to ground.

-Hal
 
First I would check for things like pinched wires, but it could be the lights. How many lights are there? Do the lights have any L-G or N-G filter caps in their power supply?
 
The circuit has no issues when its on a standard breaker.
then Like Hal said you have a N-G connection somewhere or a driver leaking current.
you said you tried one light at a time did you disconnect all light and And see if it held. If it does just start at the first one and work from their.
 
Nearly 20 years ago, I had an issue with LV track lights tripping GFCI receptacles. Had to move the circuit to opposite phase from lights.
 