eestudent

Member
Suppose you have a Lighting Panel with 3 phase, 4 wire, 415/240v 30kva,
with an unbalaced (lighting) load on each phase (L1N, L2N,L3N). Is it correct to get the largest unbalanced load then multiply it by 1.25 then divide the answer by 80%? What is the reason behind this approach? Could anyone give me a reference (Codes and the likes). Thank you very much.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
1.25 and 80% are reciprocals. Multiplying by 1.25 and then dividing by 80% would be applying the same function twice. You only need to it once.

Now, multiplying by 1.25 and then multiplying by 80% would give you the original number again.

1.25 = 5/4
0.8 = 4/5
5/4 x 4/5 = 1
1.25 x 0.8 = 1
 

bsh

Senior Member
NEC 210.19(A). I usually assume that the load is continuous and size the circuit for 125% of the load.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
bsh said:
NEC 210.19(A). I usually assume that the load is continuous and size the circuit for 125% of the load.
Not an unreasonable approach. it also gives you some headroom in case the load increases by a small amount down the road.
 