One would think whoever designed the lightning protection system would be the correct person to ask such a question.What is that standard for a good ground reading for a lightning protection system? Is it 25 ohms per rod and what should it be for the overall system?
I am getting a reading of 100 ohms on my system. What measures can be taken to rectify this?
Sent from my moto e using Tapatalk
Thanks, I didn't want to assume. I admit I don't know much outside of NFPA 70, and only a little inside of NFPA 70.A lightning protection system is a different standard from the NEC, and the NEC does not require 25 ohms. There are methods to reduce ground resistance, chemical rods, deeper rods, and those are beyond the scope of what we typically answer. As pointed out, ask the company who designed your system.
4.13 Grounding Electrodes, in NFPA 780, Installation of Lighting Protection Systems, does not specify any minimum resistances or any resistance testing for a lighting protection grounding electrode systems.
cu coated and ss rods are used for corrosion protection, not lowering resistance. Cu listed rods have a thicker cladding
Mike holt has a video showing testing resistance of ground rods driven to 50 ft. He was showing different ways of measuring GR resistanceTom, are we talking 20’ or sinking rods farther than that or a grid of 2 or more at 20’?