I am not aware of any section of the NEC, NFPA 99 or NFPA 780 that indicates what you are stating to be true. In fact, it would violate Section 250.30(A)(7)(2) of the NEC if (1) were not present. Even if (1) was utilized, (2) would have to be bonded to the system anyway.
There would be NO compliant method to ground a SDS without that system being bonded to the LPS grounding system at some point. A SDS isolated from the LPS system would likely be a greater potential hazard than any reason one might have come up with this idea...
Keep in mind the purpose of the NFPA 780 is much the same reason an SDS must be grounded as indicated in 250.4(A)(1).