chris kennedy said:The name of the company is Bonded Lightning Protection. The estimated job value on the permit app was $2900. Multiply that by 1.3, 1.5, 2?
It passed inspection today but lets play "Spot the Violation" for the heck of it.
View attachment 1314
View attachment 1315
I'm willing to concede that the installer was wearing shoes.HighWirey said:Never done cold bending of PVC but was always under the impression that a shoe was required somewhere in the process?
Well, they got busted and had to change the 90's. At the very least there was a violation of352.24. Very nice install.:roll:weressl said:The bending radius of the downcomers is insufficient.
The conduit rises ABOVE the lightning receptors, thus making them ineffective.
The installation is a typical example of highway robbery.
chris kennedy said:Well, they got busted and had to change the 90's. At the very least there was a violation of352.24. Very nice install.:roll:
View attachment 1905
electricalperson said:nice pipe bends.
why would a generator need lightning protection like that. wouldnt it make more sense to put those rods on the building its serving. i think thegenerator might suffer a little damage if its struck by lightning like that
weressl said:Step hazard.
The horizontal portion of the conduit is not supported.
There is no vibration relief from the generator to the stationary concrete pad, the conduit will break up.