hurk27
Senior Member
- Location
- Portage, Indiana NEC: 2008
I agree, this is true at the point of service, however consider , the protection downstream, for eg., a submersible pump installed 200ft below grade. The casing of the pump would be at a lower grounding impedance than the service ground. Since service grounding impedance cannot change during a fast rising surge due to inductance, the potential difference between the winding, which is reference to the system ground, and the grounded motor frame, would become enough to cause an insulation failure. Thus L-G, L-G-L & N-G connection of SPD is very crucial .
If lightning takes the path to the well casing after striking the house or service, it will to some extent treat the conductors running to this well as a single grounding conductor, while SPDs might give some relief between line and grounded conductor which could limit some damage, I highly doubt that it would protect a cable feeding this well, I have seen a few hits like this and there was nothing left of the UF feeding the well, along with the control box for it, and also only a direct strike will be trying to return to Earth as I have said before, which I don't see a MOV withstanding a direct strike, Its wishful thinking if you do.
Now if the circuit was run in a metallic raceway and this raceway was bonded to this casing, you might have a better chance, around here most well casings are PVC plastic,so very few motors are spared, even with SPD's