After speaking with one of our lead marketing engineers about your situation, we’d recommend trying surge protection device - TTC-6-1X2-F-M-24DC-UT-I – 2906764, at least on your analog input channels. This product has a lower voltage threshold and should therefore clamp sooner on transient voltages. This ought to be helpful given that your analog channels are particularly sensitive. If you still have input channels fail with this device, it’s possible you have some sort of disturbance on your ground circuit.
PHOENIX CONTACT | Surge protection device - TTC-6-1X2-F-M-24DC-UT-I - 2906764
In regards to the status indicator on these surge protectors, I was informed that it more likely to be triggered by an overload event rather than a true surge event. You can see the written response I received below.
The TTC-6-2X1-F-M-24DC-UT-I (2906767) SPD is equipped with an "overload" status indicator that operates Independently of the FMRS set. An overload status indicator alerts equipment users when the suppressor is damaged by a sustained input power source voltage that exceeds its maximum operation voltage value.
If, for example, 120 VAC was mistakenly applied to the TTC-6-2X1-F-M-24DC-UT-I that operates on 24 VDC, it would be inappropriately driven into continuous current conduction and likely suffer damage. Its overload protection circuits would engage and electrically remove the suppressor from the circuit as it transitioned to its end of life in a controlled and safe manner.