You cited some Army grounding parameters, and likened it to the 10' elevation problem we discussed earlier. I explained that bonding can't fix all problems that contractors or cable installers create. The performance of air terminals and ground rods does not cover that scenario as I think you suggested.
There's no contradiction that 10' of elevation can have a voltage potential unsurmountable by common bonding, while air terminals can be hundreds of feet above ground potential and work as designed.
We exit communications towers with feedlines above ground potential sometimes, when it is necessary to do so. But even a few feet above ground (elevation = potential) make catastrophic problems if not properly controlled further down the line. The down-conductors from air terminals to earth ground generally have much more surface area than the tiny #6 bonding jumper that NEC requires. The down conductors further connect to many earthing systems, where the lowly bonding jumper assumes by the rules that it can equalize massive potential differences between poorly constructed systems. Sadly, a #6 or even #00 can do no such miracles.
Bonding cannot protect a homeowner from poor construction practices either, such as separate utility entrance and/or ground rod locations. This is true in spite of the code allowing it, as long as that magical bonding jumper is installed. Reading the details of NFPA-780 go part of the way toward explaining the inadequacies of using only art.250 grounding, and then assuming that there is some form of lightning protection included therein.
Where 100,000's v potential is concerned, the surface of the earth will be so saturated that voltage division among many shallow conductors is more effective than one or two deep ones. DC rules just don't cover the behavior of a strike, although they are always a necessary first part of any protection equation.
Roofs of single family residences are not usually struck by lightning, and therefore most homes have no specific lightning protection. Proper code installation of service entrance and single point earth (or ufer) ground will protect them from "average" surges coming in from a nearby utility strike, tree strike, etc. Protect here means not start a fire, but they may lose all their electronics, etc.
But when a structure is located such that it CAN be struck by lightning, it can still be protected from both fire and electrical damage, it just costs more to provide this! I know some of you want to know why the soothsayers go around saying "nothing protects from a direct strike"! Well they are only right when mistakes are made in the design and construction, mistakes that lightning is unforgiving toward.
No sophisticated design or protection scheme can make up for major goofs such as the cable modem grounded to the cold water pipe, satellite dish on its own separate ground (and not bonded), etc.
Every case I have seen or read about has such an underlying cause - a mistake or underestimation was made somewhere, and lightning exploited it. Engineers have designed elaborate surge protection schemes to protect equipment, and then neglected air terminals on the structures that house our watchstanders. Go figure.