Five homes is no problem, neither is fifteen if the system is built correctly. :smile:
That was the problem, when the system was originally built, the transformer was sufficient, as more and more loads were added the system was not upgraded. Wired a store that originally had a 400 amp service, the load had grown to 380 amps per leg on the service with the voltage dropping down to a constant 105 volts during peak load, POCO had 4/0 AL service lateral at 200'
Upgraded service to 1200 amp, POCO wanted to install (2)-4/0 service laterals. Load was also being increased due to doubling the size of the store. Met with the engineers and explained the problem they were causing, and they agreed to upgrade to parallel 350 Kcmil and also upgrade transformer size. Voltage now at acceptable levels.