I’m trying to get some advice on a request from my employer to install lights within two shower stalls with a slanted ceiling 88” inches at highest point and 77” inches from floor at lowest point. Standard 120v lighting 1 phase 15 ampere circuit
The walls are surrounded with sheet metal
I haven’t get checked the NEC code book for lighting in a place like this but I assume there are height requirements for lighting directly above showers, GFCI protection for branch circuit, wet listed supplies, etc
If I bring a GFCI into a 2 gang box and then power the lighting on the load side of the GFCI will this suffice
Then I must also figure out the proper wet listed wiring method for the branch circuits while transferring from romex nm cable in the hall ceiling to the shower stalls “wet location” perhaps liquid tight?