Lights Near A Fountain
abetovr
Hi everyone,
A customer wants to install low voltage landscaping lights around a fountain. Equipment is all UL1838 listed.
NEC 411 says I can't put anything nearer tan 10 ft of a Pool, SPA and Fountain unless allowed by NEC 680.
NEC 680-I doesn't says anything about lighting.
NEC 680-II is about pools, and is very detailed on what can/can't be done near a pool, how closer could I get with a lighting installation, and whatever.
NEC 680-V is about fountains, and only talks about submersible lights inside the fountain. Does not says anything about lights outside. I didn't found any text telling that I can?t do it, nor any text that I can.
Also, 680-V only states that submersible lights shall have GFCI, be less than 150 V, and be installed in chapter 3 raceways, all of which I would do.
Given the above conditions, I am tempted to believe that I can do it. (Sometimes NEC is SO terrible confusing!!! :confused: )
Finally, tried searching the UL white book and found only references to submersible lights for fountains, and nothing about lights outside the fountain.
So what do you all think, can I or can I not install Low Voltage landscape lamps less than 10 ft of a Fountain? What would be your NEC interpretation on the subject? Has anyone had an AHJ explain 680-V in simple terms?
Are there UL or other standards that apply to this installation?
Alberto
Per sec 411.4(B) 10' . Look at 680.1 definition of a fountain. A fountain by definition is a pool. (not drinking fountain) now look at section 680.22 (B) (1) for new outdoor installation clearances.
As far as I undertand the Code text:
...A fountain might/might not be treated as a pool.
If water from the fountain ends up/is common to a pool, then NEC is clear: it?s a pool, and we have to follow 680-II
But if it is not intended for people to swim or wade, then 680-V applies.
On this particular case, customer has this stream of water, about 1 ft wide and 4" deep that goes form one place to another. So its impossible to swim on it... It is not intended for people to wade on it either.
Alberto
I think that this would be a good question for your local AHJ. It would be an interpretation of section 680.50. Does it have water common to a pool?
No, there's no pool at all.
It's just a little garden/decorative space with plants and this water stream in the middle. And it is all located within a building... (You know, those crazy things architects do)
No person would be allowed to enter the garden. The architectural design even has a sort of fence around to avoid people entering...
Alberto