Lights went out in Walmart
WHY MAIN LINE SWITCHES TRIP:
1. Modern Switchboards have incorporated many optional protection schemes in addition to standard OCPs and GFP there is blown fuse protection, normally 3-KAZ fuses in parallel with the main fuses if the a main fuse blows the parallel KAZ blows and a spring actuator pops up to operate a microswitch resulting in operation of the Main Line Switch shunt. In addition the following or a combination of the following may be installed, phase relays, under voltage relays, and reverse phase relays to offer loads on the distribution system protection.
2. So prior to chasing a Ground Fault, one has to determine if the Switch operation was a result of a blown fuse, UV or phase loss. While the blown fuse operation is simple to find, it is obvious when you look at the KAZ and additionally some Switchboards have blown fuse indication lights on the front of the Switchboard. Phase loss and UV operation can be more difficult to diagnose, if the power is restored when you arrive on site.
3. Some GFP relays have indicators that will not allow you to close the Main Switch without resetting the indicator, others allow you to close the Main Switch with the indicator still showing a GFP operation and other GFPs systems have no indication of operation, leaving you to guess the reason the Main Switch opened.
4. In order of operation based upon personnel experience for Main Line Switch opening.
a. Electricians tracing circuits short a 408/277 VAC branch circuit, or electricians or others as part of construction short a 480/277 VAC circuit. Electricians that are still tracing circuits in this method are NOT electricians. *1 see below
b. Faulty equipment shorts to ground; number one here is motors, with cooling tower fan motors being number one, HVAC compressors number two. *2 see below
c. An actual ground fault with water leading the list for the cause of the ground fault.
d. A defective GFP relay or other protection device, defective CT or an open in the CT secondary wiring.
e. A fault in 208/120 VAC distribution in a properly installed system will not operate a 480/277 GFP
5. *1 In a typical office building the majority of branch circuit breakers are 20 amp and 30 amp, if the GFP relay is set at the 100, 200, or 300 amp setting a fault on a 20 or 30 amp branch circuit can result in an operation of the Main Line Switch. A standard molded case circuit breaker will operate in the instantaneous range at 6 to 10 times the rating of the CB 10X20=200 or 30X10=300, plus or minus 35% accuracy. So if the GFP relay is set low a majority of the branch circuits can result in a GFP operation. IMO this is not good safe coordination, I feel 400 amps should be a minimum (BUT I AM NOT AN ENGINEER).
6. *2 with motor faults and large equipment faults it is almost impossible to coordinate the GFP with the OCP for the utilization equipment. Assuming the same 6-10 times instantaneous rating of the OCP a 100 amp OCP would operate on a ground fault at around 1000-1200 amps which may be at or above the GFP relay settings (maximum setting 1200 amps).
HOW TO SAFELY RESET GFP PROTECTED MAIN LINE SWITCHES:
1. Try to determine if the Switch opened from GFP operation or other system protection device.
2. Ask if there is any on going construction.
3. Ask if the Switch opened at dusk, outside lighting can be an issue especially after periods of rain.
4. Check the GFP settings time and current, write them down.
5. Have someone (because it requires a lot of walking) shut off all downstream devices at the level below the Main.
6. Once you are sure the power is off, open and test the bus with a tester you are sure works (HAVE YOU TESTED YOUR TESTER). It is possible for Switches to hang up BECAREFUL.
7. Inspect the bus for any water and signs of a fault.
8. Megger the bus phase to phase and phase to ground, if the reading is low check that there are no relays connected to the bus, bus taps or other loads you are unaware of. Normally we test the bus at 100 VDC first to avoid damaging protective relays such as Phase or UV relays the retest at 1000 VDC. We?d like a reading above 50 megohms, 5 can be acceptable, .5 as recommended by some IS NOT ACCEPTABLE, IMO.
9. Open the next downstream OCP and then megger the feeders. Continue in this manner.
10. With HVAC equipment, motor loads, large duct heaters and other utilization equipment you will need to get to the load conductors for the equipment, do a visual on the equipment looking for signs of a fault.
11. Check for blown fuses and opened CBs as you work your way through the building.
12. Hopefully you will located the source of the fault, if you don?t the problem may be with the relay and require testing, and this is more than just pushing a button. A high current test set is required.
13. If you have done all of the above, with exception of item 12, you may have to close the Main Switch without resolving the issue, THIS IS CONTRAVERSAL and may violate local and federal rulings, BUT IMO is sometimes the only solution when all avenues have been exhausted.
a. Set the GFP relay to 100 amps (or lowest setting) and the time delay to the lowest time setting Instantaneous, .1 or minimum are typical minimum settings.
b. READ THE SWITCH OPERATION Instructions, the number of Service calls we receive for damaged Switches due to improper operation exceeds a level that would be obtained if Electricians READ THE INSTRUCTION.
c. With all downstream OCPs open, all covers installed on the Switchboard, all cover screws installed tight, you dressed in proper safety gear and no one else in the room; close the Main Switch in such a manner that places you in as safe a position as possible.
d. If the Switch holds and it should if you have done all the above steps as noted. Move on to the next level OCP.
e. Close these devices one at a time allowing any equipment that may need to start time to start.
f. If the GFP operates at any point and you gave equipment sufficient time to start you may have located the fault.
g. Reclose the Main Switch per step 13.c. and start closing all the OCPs leaving the one with the fault off.
h. Bring the building on line and return to the OCP with the suspected fault and isolate the source of the fault.
i. One issue to be aware of is; large dry type transformers have inrush currents that can trip GFPs relays due to the inrush current are not Zero Sequence.
j. Once you have isolated the fault, remember to reset the GFP settings to the ?AS Found Settings?, reset the GFP indicator (if present).
14. If after this you have not located any problems, the GFP relay should be left set at the lower settings, the GFP tested at all presets for current, and if all checks out it may be necessary to install a 5 channel high speed disturbance analyzer to assist in determining the cause of the GFP operation.
15. NEVER remove the fuses or disable the GFP to prevent operation in order to restore power, you can and will be had liable for any deaths or damage.
16. If the cause of the GFP operation is a setting you believe is too low, ask the facility personnel for the coordination study to see what the engineer specified. Often the installing electricians leave the GFP set at the factory shipping settings which is the minimum for current and time. If a coordination study is not available (VERY TYPICAL) tell the facility representative they need to get their engineer of record to provide a setting. The normal response from engineers is what does the factory specify (NOTHING (well minimum) AS THE MANUFACTURE WANTS NO LIABILITY IN THIS ISSUE) or what do you normally set it at. My first response is I set it where the engineer tells me, then I give him my rationale for a minimum of 400 amps .1 sec. If they accept this I make them sign documentations stating it was the facilities decisions to adjust the relay settings.
Sorry, I didn't get the whole procedure for ensuring that it is safe to do a reset here..EDIT: I see it's all in the post now.
Also, kinda wondering about the different styles of main breaker you mentioned, as in a bolted pressure switch (is that a bolt-on breaker / molded case breaker?) and the high pressure contact switches? (Are those considered molded case?). I can identify a molded case breaker, but these others are new terms to me.
hello, I am the service man that got the call, been doing service now for about 12 yrs, electrical to long, it was late in the day I did not check the settings on the panel 200 amp breaker,but lets say it was at 200 or I will set it to 200 how would I check for this not to happen again Walmart hates going dark.
Hello Carlos
One in our portion of the industry should not be thinking of changing the calibration of CBers if there is calibration to change available on the CBer.
What was/is the voltage of your panel?
I am curious, how far away from the panel is the location where the fault occured?
You mention it occured twice...was the second time accidental, or did you try to do this on purpose?
I understand you are a service technician, but some of this stuff is better off letting the engineer or a properly trained electrician doing the work.
Properly trained merely means the individual has training in specified areas that another may not have training in.
these has happen before
the two pole breaker that feeds the parking lot lights, one row had a short, when we were troubleshooting the pole lights wondering if it was a ballast issue it happened again blowing the L3 fuse in the panel.this Walmart is 5yr old and all is farley new,the panel and the breaker that feeds that panel is in the same Electrical Room.
PS I will get more info tomorrow as what type of breaker.of course these breakers are controlled by Novar but all that is working correctly.
I did a post on bolted pressure switches (but to lazy to search), these are fused switches and are manufactured by Pringle (new Eaton), Square D BoltLoc and BoltSwitch. HPC are a GE Brand name.
Squar D
Pringle
Lastly Carlos I may have misread your post if a 200 amp CB tripped and not the main it is a coordination issue you may not be able to overcome (short of working SAFE). But if the main tripped (1000 amps or higher at 480 VAC) then the above should be relevant.
Brian: thank you for your detailed post on resetting GFP.
Most electricians when they see a tripped breaker immediately reset it, that's what we do. But that breaker tripped for a reason.
Carlos: I understand your frustration in getting this fixed.
For a while I had a signature that said "the more I know the less I know".
480/277 Volt systems are very dicey in a ground fault, which why we have GFP. I have seen pictures of melted rigid conduit from a ground fault.
Tom I have been in electric rooms with nothing but a pile of twisted smoking metal that does not resemble anything close to switchgear, all due to a arcing ground fault and the GFP was disabled.
Pringle after a major fault. The switch opened from a downstream fault (water in the switchboard) and the switch was reclosed into a fault.
Brian,
As with Pierre hope no injuries. also, where did this happen? I am on a crusade in DC existing conditions to have all foreign piping (110.26(F) and 96' 384-4 above gear relocated or proper leak apparatus installed. The building engineers have really appreciated my stand on this and are working on it.
In Virginia.
Did a 22 hour Sunday for a flood, outside air vent stuck in electric sub station and sprinkler pipe froze, then broke and flooded 480 VAC gear and several ATS's.
Good luck DC fire marshal is tough on sprinklers over gear trying to promote business I guess, also the practice of covering the gear is USELESS as when the water hits the fire the steam permeates everything.
May I suggest THIS ONE to start?
And THIS ONE....
Again let me apologize for the misunderstanding,again Ive been around for awhile and I really missed the BIG PICTURE and you knocked some of the spider web OFF over my eyes,this time I was lucky that we did not have any arch flash and I was standing in front of that panel when the Novar System energized the Pole lights,you have a nice Day and you be careful on that bike.
I will be posting pictures and all details concerning this issue.
Probably now trying to stare at the nurse thru the gauze or staring at the job section in the paper...
To our surprise when the breaker tripped it did not make any noise just like a regular trip, we did find the problem why it was tripping,the two #8 wires feeding that breaker were damaged inside the pvc conduit causing phase to phase we believe since its not an overload the breaker on the panel did not have time to trip but we still have the issue why the 200 amp breaker feeding that panel tripped before the 200 breaker on the panel, it should just trip the two pole at the panel.
I will be posting breaker IEC info and pictures on my web site soon, I appreciate the concern.
Squar D
Pringle
the 3 pole 200 amp breaker that feeds the 200 amp 277 lighting panel tripped instead of just the two pole 20 in the panel, we corrected the damaged wire in the pvc conduit causing that breaker to Tripp we still have the issue why the 200 amp in the panel did not trippe and caused the 3 pole feeding that panel to trippe,I will be posting IEC info of the two breakers involved and pictures on my web site soon.
No problem sir, I thank you for posting this publicly. :)
I look forward to finding out what you find out on this issue..I'm leaning toward coordination issues. In other words, the trip curve for instantaneous (i.e. like short circuit) current on the 200 amp main is probably quicker that that of the 20 amp DP you were dealing with.
I really learned a lot from your post Brian John. Thank you ,for sharing that.
Thank you for the kind words I really want to be a teacher but a lack of education and the fact my family could not live on that wage keeps me in the trade.