Is there a limit on how many 90's can be installed in a conduit run.
peter said:Mr. Valdez,
You don't always have to use a conduit body or condulet. Often you can get by with using an ordinary box which is much [75%] cheaper.
But the main thing to realize is that you will eventually have to pull wires through it and, the fewer the bends, the easier the pull. If you put some thought into it, you should be able to make the entire run with three 90? bends. And, if you can, make them super radius bends.
~Peter
Jim W in Tampa said:Just how do you arive at only 3 90's ?
infinity said:Only 3-90's? I wish that were always true. It would put the pullbox and condulet guys out of business.![]()
georgeswe said:360 is the MAX however you get to that, make sure to take in account box offsets and such.
Trust me If the max was anything over 360 you wouldnt want to go over it anyways.
3 #12s in a 3/4 conduit can be a royal pain in the ass to pull in in anything 360 deg +.
peter said:And, if you can, make them super radius bends.
~Peter
peter said:Mr. Valdez,
You don't always have to use a conduit body or condulet. Often you can get by with using an ordinary box which is much [75%] cheaper.
But the main thing to realize is that you will eventually have to pull wires through it and, the fewer the bends, the easier the pull. If you put some thought into it, you should be able to make the entire run with three 90? bends. And, if you can, make them super radius bends.
~Peter
don_resqcapt19 said:Trevor,
When you do that, do you calculate the sidewall pressure to make sure that the insulation is not being damaged by the crushing force that is created when pulling around the 90s?