Trevor,
There is a pulling calculator here. It is a bit difficult to use as you have to do each straight section and each bend as a seperate calculation.
Don
That will make a big difference in the pulling force which is directly related to the sidewall pressure. With a more nomal run with that many 90s it is very likely that the sidewall pressure limit will be exceeded on the last few 90s. This damage may not show up at the time of installation, but may cause insulation failure in the future.The run I mentioned had a vertical section of about 70' feet with a few of the 90's. In that section of the run, the weight of the conductors made them literally feed themselves.
With the cost of copper, you really need to look at the pulling tension and sidewall pressure. In most cases the limiting factor is not the pulling tension, but the sidewall pressure. High sidewall pressure is one reason to use large radius bends as the side wall pressure is equal to the pulling tension at the end of the bend divided by the radius of the bend in feet.Each run is evaluated in the field based on length of run, conduit fill, etc.
There is a pulling calculator here. It is a bit difficult to use as you have to do each straight section and each bend as a seperate calculation.
Don