line and load conductors in same raceway

Status
Not open for further replies.

sparkmantoo

Member
Location
Virginia
a 1ph 208v circuit feeds a disconnect. the disconnect is for a fan. if you run the line and load wires in the same raceway, do you count all of the conductors as current carrying, or do you only count one set?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Re: line and load conductors in same raceway

You count them all. They all produce heat the derating is intented to limit the heat produced in the raceway.
Don
 
Status
Not open for further replies.
Top