S sparkmantoo Member Location Virginia Apr 12, 2003 #1 a 1ph 208v circuit feeds a disconnect. the disconnect is for a fan. if you run the line and load wires in the same raceway, do you count all of the conductors as current carrying, or do you only count one set?
a 1ph 208v circuit feeds a disconnect. the disconnect is for a fan. if you run the line and load wires in the same raceway, do you count all of the conductors as current carrying, or do you only count one set?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Apr 13, 2003 #2 Re: line and load conductors in same raceway You count them all. They all produce heat the derating is intented to limit the heat produced in the raceway. Don
Re: line and load conductors in same raceway You count them all. They all produce heat the derating is intented to limit the heat produced in the raceway. Don
S sparkmantoo Member Location Virginia Apr 15, 2003 #3 Re: line and load conductors in same raceway thanks.