Shall Be 300.3 (C) Conductors of Different systems
Do CAT5 and RG6 have at least 240V insulation?
Shall Be 300.3 (C) Conductors of Different systems
Do CAT5 and RG6 have at least 240V insulation?
Do CAT5 and RG6 have at least 240V insulation?
Chris, in this picture (120-volt receptacle) wouldn't they only need to have insulation rating of 120-volts and be a class 1 circuit, not class 2 or 3 (which I don't think they are class 1 circuits).
Yes sir, but the Isotec cable comes in multi conductor assemblies, allowing for voltages higher that 120.
Since the 120 volt power is in a cable and not individual conductors the other cables could have an insulation value of 1 volt and this still would be code compliant.
So I could run romex and cat-5/RG-6 in the came conduit? That is essentially what it is there....Since the 120 volt power is in a cable and not individual conductors the other cables could have an insulation value of 1 volt and this still would be code compliant.
So I could run romex and cat-5/RG-6 in the came conduit? That is essentially what it is there....
That's an excellent point Rob. What about 725.136(A)? Can what was shown in the OP get around it technically also?
SIMTRA? cables feature patented, ferrite-barrier technology
Lou, I think the manufacturer has supplied the barrier required by 725.136(B)
Based on 725.136((I)(2) & 820.133(A)(2)ex#1, this is a permitted installation. 300.3(C)(1) has no bearing on this installation, it has been modified by the above sections.
*Chapters 1-4 are general and can be modified by Chapters 5 - 7, and Chapter 8 is not subject to Chapters 1-7 unless specifically referenced.
...separated.... by a continuous and firmly fixed nonconductor, such as porcelain tubes or flexible tubing, in addition to the insulation on the conductors.
I think there may be an arguement that we are outside the scope of this code section, but I see your point.This article covers coaxial cable distribution of radio frequency signals typically employed in community antenna television (CATV) systems.
Lou,If the non 120-volt circuits are class 2 or 3, then 725.136(A).
(A) General. Cables and conductors of Class 2 and Class 3 circuits shall not be placed in any cable, cable tray, compartment, enclosure, manhole, outlet box, device box, raceway, or similar fitting with conductors of electric light, power, Class 1, non?power-limited fire alarm circuits, and medium-power network-powered broadband communications circuits unless permitted by 725.136(B) through (I).
Lawyers at least have the benefit of the Supreme Court to make decisions!I feel like I'm going to law school. :smile:
For both Articles, look under Other Applications, the 1st exception.
Look specifically for the terms "nonmetallic-sheathed".
You will notice in the picture, that the TC cable shown is listed as being manufactured with a nonmetallic-sheath.