A supply side connection is not it's own service unless there's a new service point
But you still have to contend with 230.72(A), which seemingly says that all the disconnects permitted in 230.71 have to be grouped.
Is PV the additional service allowed by 230.2(A)(5)?
Or is it the additional set of SECs allowed by 230.40 Exception 3? (PV = accessory structure)
I say it is both.
When you have an extra set of SECs, isn't that also another service?
So either way, PV is an additional service when supply side.
"for each shall consist of 6"..."six sets of disconnects per service" means you can have 6 for loads and 6 for supply side PV.
You can have 2 sets of discos with 6 discos grouped together for each, each set of 6 can be in a different place (like inside/outside).
230.71 Maximum Number of Disconnects.
(A) General. The service disconnecting means
for each
service permitted by 230.2, or
for each set of service entrance
conductors permitted by 230.40, Exception No.1,
3, 4, or 5, shall consist of not more than six switches or sets
of circuit breakers, or a combination of not more than six
switches and sets of circuit breakers, mounted in a single
enclosure, in a group of separate. enclosures, or in or on a
switchboard or in switchgear. There shall be not more than
six sets of disconnects per service grouped in anyone location.
230.72 Grouping of Disconnects.
(A) General. (My note: EACH SET OF) The two to six disconnects as permitted in 230.71 shall be grouped.
---
230.2 Number of Services. A building or other structure
served shall be supplied by only one service unless permitted
in 230.2(A) through (D).
(A) Special Conditions. Additional services shall be permitted to supply the following:
(5) Parallel power production systems
--
230.40 Number of Service-Entrance Conductor Sets.
Each service drop, set of overhead service conductors, set
of underground service conductors, or service lateral shall
supply only one set of service-entrance conductors.
Exception No.3: A single-family dwelling unit and its
accessory structures shall be permitted to have one set of
service-entrance conductors run to each from a single service
drop, set of overhead service conductors, set of underground
service conductors, or service lateral.