Line Side Grounding

Status
Not open for further replies.

Gategator37

Senior Member
I have a MDP with self made knockouts, if I have (2) 4" rigids supplying this MDP and 2 locknuts on each raceway do I need bonding bushings or would these locknuts be considered "bonded" or do i need locknuts rated for bonding?
 
You could use one bonding locknut or bonding wedge on each raceway. It doesn't have to be a bonding bushing.
 
Status
Not open for further replies.
Top