ggunn
PE (Electrical), NABCEP certified
- Location
- Austin, TX, USA
- Occupation
- Consulting Electrical Engineer - Photovoltaic Systems
As a practical question, I don't know the answer. As a matter of code, I think that you can argue that PV is not a load and therefore doesn't fall under 230.40 Exception 2, which specifically refers to separate loads.
Not if the PV isn't a load. And not if its permitted under Exception 5 instead of Exception 2.
Is this an ironclad argument? Maybe not, especially if the inverter has a nighttime standby load. (It may or may not). But it's got a valid logic to it, and is the best argument to use with this AHJ.
From the data sheet, the internal consumption at night of an SMA SB 8000 is 0.1W. At 277V, that's less than 0.0004A. Is that a load? Well, yes, but seriously?