We have a residential install with a line side tap where the max output of the inverter x 1.25 = 26.25A. The fused AC disco is 30A rated with 30A fuses.
We had an engineering firm assess the project and they stated that the AC disco must have a minimum rating of 60A based on NEC 230.79 (D).
From what I can see, and I'm not an expert at parsing code, our system should be ok based on 230.79 (A) or (B) since our PV system is one single branch circuit.
Since (A) does not mention how many wires in the circuit we might be more aligned with (B) which specifies "2-wire" circuits, which ours is as it is a 240V output.
NEC 230.79 (D) which they quoted as the relevant section says that "All Others" shall have a rating of not less than 60 amperes.
Are we a 2-wire branch circuit or are we an "Other"?
Thanks.
We had an engineering firm assess the project and they stated that the AC disco must have a minimum rating of 60A based on NEC 230.79 (D).
From what I can see, and I'm not an expert at parsing code, our system should be ok based on 230.79 (A) or (B) since our PV system is one single branch circuit.
Since (A) does not mention how many wires in the circuit we might be more aligned with (B) which specifies "2-wire" circuits, which ours is as it is a 240V output.
NEC 230.79 (D) which they quoted as the relevant section says that "All Others" shall have a rating of not less than 60 amperes.
Are we a 2-wire branch circuit or are we an "Other"?
Thanks.