Line side tap of an MLO panel for PV system install

Status
Not open for further replies.

wrobotronic

Senior Member
Location
Colorado
this is one of those things that my gut tells me was wrong.

A new PV install has a line side tap on the conductors feeding the house. Pretty normal. However, the main panel does not have a disco to de-energize the bus.

i failed the installation and stated a main was required because the system was modified. I DO NOT have a code reference for this judgement, however. There are 15 or more breakers on the panel too, So the six handle rule does not apply.

Can I enforce the addition of the main breaker? If so, is there a code reference for this that I could use?

This seems like a serious safety issue to not have a main. Thank you all for the help.
 
Well it turns out that this type of GE panel has a split bus and it does in fact meet the requirements of the 6 handle rule.

i don't like it, but it's not about what I like or don't like...lol
 