On a PV system a line side tap is allowed under an exception. Duz this tap need to be before the first disco. or, can it be between two discos?
On a PV system a line side tap is allowed under an exception. Duz this tap need to be before the first disco. or, can it be between two discos?
Depends on the meter/main combo. Some have provisions (such as having two mains or an optional accessory second main), some can be tapped through listed accessory modifications (rare), some (most) cannot. For the latter, rearrangement could be "simple" as replacement with one of the former.So................if there is no room, due to a meter socket, disconnect combo. One would have to rearrange the service?
There is no formal definition of a line side (i.e. service) tap, but I believe everyone accepts that it is any service conductor which has ampacity less than the service rating....
Some may argue that this doesn't formally meet the definition of a tap. In my opinion, a tap is the best model we have for it. It is a section of conductor that is only protected in excess of its ampacity, and follows specific rules to minimize overload damage as much as possible.
Only applies to a feeder tap.In any case, follow the tap rules of 240.21(B), size the EGC per the feeder or service, and you have to terminate in a dedicated OCPD and integral/adjacent disconnecting means for the PV system.
There is no formal definition of a line side (i.e. service) tap, but I believe everyone accepts that it is any service conductor which has ampacity less than the service rating.
Only applies to a feeder tap.
Sizing ungrounded conductors is no different than circuits in general, but reaching that conclusion is most certainly not straightforward. While debate abounds whether the PV System disconnect is a Service Disconnecting Means, I believe everyone agrees that the line side conductors are considered service-entrance conductors. The tricky part is that service-entrance conductors size and rating are required to be based on Article 220 calculated load. As you know, PV Systems present essentially no load to the service. However, considering the PV system's load is service connected loads or the service itself, we conclude these ungrounded conductors must be sized and rated not less than the PV system side of the disconnect.So in the event of a supply-side service tap, what is the sizing procedure for the tap circuit wiring, EGC's, GEC's, and where (if anywhere) neutral/ground need to be bonded?
If it is different from the sizing of the circuit in general.