1- Would the the disconnect that the taps feed be required to have a GES.
2- I believe this is now a service disconnect
1- All I can really say about that is- the truth is out there. :huh:
The problem being that code doesn't really say, so your AHJ can interpret it any way they choose.
The way I understand it (around here) is you want a GEC *to the* existing GES from your PV disco, N and EGC are bonded in PV disco.
So-
N bonded to G in main service panel, N bonded to G in PV disco, GECs from both to GES.
Around here, the POCO changed it back in January to require a dual meter (for PV feed-in-tariff output/site usage), the neutrals coming out of the meter sockets to the service panel and PV disco are both bonded to the meter can, so...
The POCO now kind of forces you to set it up as italicized above.
No more junction boxes, and I'm fine with that.
2- To me, of course it is.
There is a service to the house.
You connect the PV to the service conductors or service entrance conductors on the line side.
You have a PV disco switch.
It disconnects the PV from the service conductors.
Therefore, it's a service disconnect.
It disconnects the service from the PV connected to said service.
I can't understand why power being produced as opposed to consumed makes any difference.
If anyone has any theories as to why it would matter if power is coming into vs. going out from the premises, I'd love to hear them.
I'll say it again- the inverter does consume a tiny amount of watts at night, and I don't see a reason to wire it differently just because there is 3000w going out when the sun is up.