Our premises system needs 50 amps to operate.
Sent from my iPhone using Tapatalk
Sent from my iPhone using Tapatalk
Sorry for yelling...just frustrated this is still an issue. It has been a problem in my world for multiple Code cycles now.
If it were my system to design I would have cleared this with the AHJ in a precon meeting before building it. It is far easier to design a system to the necessary specs than it is to fix it or fight about it after it is built. Good luck with your inspection.For what it's worth I appreciate everyone's input.
No disrespect towards anyone when I say interpretations + theory+preference can make these type of installs sometimes not worth getting involved in.
We put taps in the first panel. L1 L2 line side of the breaker. Neutral landed on neutral bar. Ground landed on same bar , feeding a 60 amp service rated disconnect with 50 amp fuses. Neutral and ground bonded in the disconnect feeding the PV equipment.
Will the pass? I'll know today or tomorrow when the 5 installs are inspected.
I'll will post the outcome when I find out. Unfortunately it won't change much about about the disagreements here but maybe it'll help others see how these set ups are viewed in different areas.
Thanks
Sent from my iPhone using Tapatalk
For what it's worth I appreciate everyone's input.
No disrespect towards anyone when I say interpretations + theory+preference can make these type of installs sometimes not worth getting involved in.
We put taps in the first panel. L1 L2 line side of the breaker. Neutral landed on neutral bar. Ground landed on same bar , feeding a 60 amp service rated disconnect with 50 amp fuses. Neutral and ground bonded in the disconnect feeding the PV equipment.
Will the pass? I'll know today or tomorrow when the 5 installs are inspected.
I'll will post the outcome when I find out. Unfortunately it won't change much about about the disagreements here but maybe it'll help others see how these set ups are viewed in different areas.
Thanks
Sounds good to me. In my opinion, better to put in the green screw and then be able to take it out if the inspector asks than to lose track of it and then have the inspector ask you to put it in.![]()