Hi, I have two questions that I hope the experts in this forum can shed light on. First, does Insulation-piercing tap splice connectors act like a CT?
That is, a CT normally reduces the current from a high amperage say 100 amp to a much smaller and hence measurable amperage say 5 amp. CTs can be both for measuring and for overcurrent protection. In the latter the CTs are normally connected to a relay then to a contactor/circuit breaker. When the utility current reaches dangerous levels then the CTs will send a signal to the relay and then the relay to the contactor/cb to open the circuit. With a line side tap these insulators are used and the tap connectors are connected to line of fused disconnect, OCPD. Does this mean that the Insulation-piercing tap splice connectors are really CTS rather than reduce the voltage?
Second, There are now two different current sources passing though the fuses. The utility current at Line and the Inverter ac output at Load. Should this not cause the two current sources to burn themselves out and activate the fuse or Is there a meshing of both currents so that they are safely passing through the fuses?
That is, a CT normally reduces the current from a high amperage say 100 amp to a much smaller and hence measurable amperage say 5 amp. CTs can be both for measuring and for overcurrent protection. In the latter the CTs are normally connected to a relay then to a contactor/circuit breaker. When the utility current reaches dangerous levels then the CTs will send a signal to the relay and then the relay to the contactor/cb to open the circuit. With a line side tap these insulators are used and the tap connectors are connected to line of fused disconnect, OCPD. Does this mean that the Insulation-piercing tap splice connectors are really CTS rather than reduce the voltage?
Second, There are now two different current sources passing though the fuses. The utility current at Line and the Inverter ac output at Load. Should this not cause the two current sources to burn themselves out and activate the fuse or Is there a meshing of both currents so that they are safely passing through the fuses?