Ungrounded delta secondary. 480V three phase.
Electrician took readings on factory equipment..... and on line side of main breaker. Utility company also got the same exact readings on secondary of transformer.
480V to ground on phase A
480V to ground on phase C
0 V to ground on phase B.
We all get 480V line to line as expected.
The electric company says the B phase to zero is not surprising, as there literally is no ground reference. They also say their transformer reads line to line 480V on all three phases so they are good. They don't care about line to ground simply because its ungrounded with no ground reference.
Incidentally, all electrical equipment in factory works perfect. No hiccups.
Do we agree with this or do you think there is something faulty with their transformer?
What have other people found out in this situation?
Electrician took readings on factory equipment..... and on line side of main breaker. Utility company also got the same exact readings on secondary of transformer.
480V to ground on phase A
480V to ground on phase C
0 V to ground on phase B.
We all get 480V line to line as expected.
The electric company says the B phase to zero is not surprising, as there literally is no ground reference. They also say their transformer reads line to line 480V on all three phases so they are good. They don't care about line to ground simply because its ungrounded with no ground reference.
Incidentally, all electrical equipment in factory works perfect. No hiccups.
Do we agree with this or do you think there is something faulty with their transformer?
What have other people found out in this situation?