winnie
- Springfield, MA, USA
- Electric motor research
It seems strange to me that the primary neutral is left floating. Wouldn't that cause load-dependent voltage shifts?
This is true for wye:wye transformers.
With a wye:delta transformer, circulating current on the delta acts to create a low impedance neutral. This means that a wye:delta transformer will try to hold the wye point at the neutral of the phases.
If you connect a wye:delta transformer to a 4 wire system, then the transformer will try to force the neutral wire to the neutral of the phases. This may be desirable (eg. 'effective grounding'), but will also mean lots of circulating current in the transformer.
This is why you are _not_ supposed to connect the neutral when a delta:wye transformer is used in reverse.
-Jon