Line voltage T-stat

Status
Not open for further replies.

bnb

Member
I recently serviced an apt.complex that is using a single pole LV T-stat for two 20a 220v wall mounted radiant heaters. This configuration leaves potential 120v to the unit until the t-stat closes. In my opinion this install would be more safe using a 2 pole t-stat that broke both legs to the units. What do I reccomend to the customer and is there any code issues that apply?
 

bphgravity

Senior Member
Location
Florida
Re: Line voltage T-stat

If the thermostat does not directly interrupt all the ungrounded conductors it just cannot be used as a disconnecting means.

Why do you think a 2-pole t-stat would be safer?
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: Line voltage T-stat

Expanding on Bryan's statement, there's usually no way to lock a thermostat. There are means to lock out breakers however, and a two-pole breaker can be locked out. That would be the acceptable means of disconnect. From there, if you want to use a single pole thermostat, knock yourself out.

See 424.20(B).
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: Line voltage T-stat

I agree with what Bryan and George have said. But are you really talking about using the thermostat as a disconnecting means for the heaters? Is your question more along the lines of blocking both sides of the thermostat?s connections, rather than just one side, without regard to the status of the breaker that provides 220 volt power to the heaters? Is this a maintenance issue or some other safety issue that concerns you? Like Bryan said, why do you think a 2-pole would be safer?
 

bnb

Member
Re: Line voltage T-stat

My thought would be. if a maintenence personel (who does not have as much knowledge about electric as a journeyman electrician) goes to service the unit and turns the t-stat off thinking this kills the power to the unit. He or she could potentialy get hit servicing that unit.
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
Re: Line voltage T-stat

The problem is that, in that person's opinion, that person is qualified. :eek:

That is one reason for the code: to reduce the number of opportunities that the unskilled have to hurt themselves.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: Line voltage T-stat

bnb there is no excuse for working on electric equipment without a non contact voltage checker or at least a simple volt meter.

I look at like this, once a person pulls out a tool and deliberately opens electrical equipment they have to take responsibility for their own actions, they should not be relying on any code to protect them from themselves.

There is nothing to say that even if the thermostat broke both conductors that the unit is safe to work on.

The feed may run to the heater first then a switch leg out to the thermostat. Or if the heater is large enough the thermostat may only control a contactor in the unit.
 