gar
- Ann Arbor, Michigan
- EE
130316-1440 EDT
The MTU (measuring and transmitting unit) part of a TED system measures +/- power. TED does not do a good job on low power factor. I believe this is mostly a result of the current transformers being used.
By contrast the Kill-A-Watt handles power factor very well. With a high quality 30 ufd capacitor the measurements are:
123.7 V
1.41 A
174 VA
1 W
Xc = about 90 ohms
So less than 1% power error at a phase shift of 90 deg for the current relative to voltage using Kill-A-Watt.
I have also run an unloaded single phase induction motor at constant voltage and adjusted the shunt capacitance with essentially no variation in the power reading on the Kill-A-Watt. With no capacitance the PF is 0.25 . Simultaneously TED shows a large change in the power reading from no PF correction to about full correction.
TED uses the Cirrus CS5461A chip and this should be as good as the Kill-A-Watt. Thus, my reason to put the blame on the TED current transformers. Kill-A-Watt uses a resistive shunt for current measurement, thus, no phase shift.
123.7 V
1.41 A
174 VA
1 W
Xc = about 90 ohms