I experienced my first headache last week with the new AFCI breakers. Whenever either the light or the fan was turned on the breaker tripped. Thought it was the fan, because you would have the pull chains in the off position, the circuit holds. took down fan and put a light on the circuit, and it tripped. Tried to test for continuity, no luck. At this time all wires were disconnected and tested, and my headache was "this big". My head was pounding, and i was tired, time to go home for the weekend. Next week I purchased some headache prevention"megger". Tested circuits. Let me know if im right Mark. Number keeps going up is good insulation, ground to neutral shows 0 resistance immediately . I as an apprentence "megger man" believed I have found the Evil wire. The neutral, I removed the offending wire from the receptacles it was on, and jumped a new wire across to test. Viola it worked. The megger I purched is a Fluke 1507. Oh and then I replaced the wire for real. Wires will now be tested at rough in, back charges for bad wires at trim out.