Doesn't sound like code matters here. If it does, the question is which code, kind of hard to comply with NEC when you are mixing North American and European methods together, you usually need stick with one method or the other.Regarding Autotransformers, see if they comply with 210.9, 450.4, and 450.5.
If you are complying with NEC and you have a grounded supply, you must bring the grounded conductor to the service disconnect or first disconnecting means for separately derived systems and bond all non current carrying metallic components of electrical system together to form the equipment grounding conductor. Even ungrounded systems where permitted must still have a grounding electrode and equipment grounding conductors - this to help assure equipotential between those items.In my over 1,000 relatives and friends. I haven't heard of anyone getting a shock or electrocuted. I wonder if it's because our appliances are all plastic now. What metal chassis do you use regularly in the US? The reason there is such low fatality is the reason literally no one use any grounding around the country. All haven't heard of GFCIs too. I'm just doing it just to be sure and to learn fascinating new technology.
You mentioned a lab. So you may be in a high tech facility. Can you help me think of any commercially available open neutral service detector or possible design of one using combination of RCDs (see the url in the link below). I have a single 120v apparatus in a commercial building with neutral inside. And since the utility company doesn't maintain the service neutral well because not much use it. I don't want the electricity to divert to my aircon chassis or panel chassis if the neutral service gets open or disconnected. Please see this thread and help me. http://forums.mikeholt.com/showthread.php?t=195234
If there is no solution for a detector and disconnector in case of open neutral service. Then I need to remove the only 120v item in the commercial building which is the Siemens First Surge 140,000 Surge Protector Device. It has circuits inside it that uses 120v and may be more than 5mA. Please check out the link. Many thanks for the tips below. I'll think about it while waiting words from Siemens if my Siemens GFCI (the 16 to be installed) were counterfeit.
Just because you or your thousands of friends/relatives haven't been shocked doesn't mean it won't happen when something fails.
In a dwelling with wood subfloor and nonconductive finishes there isn't much to introduce "ground" potential so if an appliance frame does become energized there may not be much for shock hazard anyway. But bring something that is at ground potential near it and you will be shocked if you touch both at same time. This may be another appliance that is grounded somehow, a water pipe, concrete floor (especially if on grade), or outdoor outlets where you are on grade when using whatever is plugged into them.