Listed factory installed unit w parallel fuses DC

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Please see attached sketch. I have listed factory installed unit that has parallel fuses 20A for + terminals which are allowed per NEC 2017 section 240.8. The unit has DC system voltage with + and - terminals. I have #12 awg 10 of them into the unit which connects to The 20A fuses 5 of them in the unit. The output conductor from unit is #3 awg (100A cable) 2 of them one for the + and other for the - terminal.

My question is the following:

1. Would the 5 - 20A fuses protect the #3 awg cable or not?

cca7a4e5020952ffcc6063a1330b8d4a.jpg
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
It appears to me that the number three conductor has an ampacity of 100 amps and is protected by 100 amps worth of overcurrent protection. I question The jumpers on the supply side connecting all the fuses together. They seem unnecessary.
 